Welcome to the International Skeptics Forum, where we discuss skepticism, critical thinking, the paranormal and science in a friendly but lively way. You are currently viewing the forum as a guest, which means you are missing out on discussing matters that are of interest to you. Please consider registering so you can gain full use of the forum features and interact with other Members. Registration is simple, fast and free! Click here to register today.
Tags electricity

Reply
Old 13th August 2017, 02:20 AM   #1
psionl0
Skeptical about skeptics
 
psionl0's Avatar
 
Join Date: Sep 2010
Location: 31°57'S 115°57'E
Posts: 11,221
120 V or 240 V Mains - which voltage is better?

Just something I have been wondering about recently.

Most appliances can just as easily be designed for 120V mains as 240V mains so it is six of one and half of the other. More heavy duty appliances will require a higher voltage and sometimes, only three-phase will do (for example, I used to have a three phase motor to pump bore water).

Most places in the world have a 240V mains. The local power lines carry that voltage on 3 lines (plus one for neutral) and it is only necessary to tap into the line to supply the house with either single phase or three phase electricity.

America, Canada, Japan and a few other countries use a 120V mains. There the setup seems a little more complicated. As I understand it, the local power lines carry 7,200V and pole top (or underground) transformers convert it to a "center tapped" 240V supply (http://science.howstuffworks.com/env...rgy/power7.htm). Each transformer supplies a single house with two phase 120V electricity (although residential complexes may share a transformer). Heavy duty appliances like washing machines can easily be accommodated with 240V but if a household needs a three phase supply then I guess they need an extra pole top transformer.

About the only advantage I can see of a 120V system is that local power lines can be thinner since they carry less current. I know an electrician who has worked in both Australia and the USA. He describes US household wiring as a "mess" and much prefers Australia's 240V system.

I was wondering if anybody involved in power distribution would like to weigh in.
__________________
"The process by which banks create money is so simple that the mind is repelled. Where something so important is involved, a deeper mystery seems only decent." - Galbraith, 1975
psionl0 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 02:28 AM   #2
Beerina
Sarcastic Conqueror of Notions
 
Beerina's Avatar
 
Join Date: Mar 2004
Posts: 28,743
It's to stop you from insta-dying if you get shocked. Or at least reduce your chances.

US houses typically have 240 available for electric stoves, and general home equipment is 120.


My dad, rest his soul, as a child (this would be mid 1940s) fell in the tub, dropping a radio in with him. My grandmother had to run down into the basement and flip the main off.

I'll leave it to you as to whether the 120 volts killed my father when he was 6 or not.
__________________
"Great innovations should not be forced [by way of] slender majorities." - Thomas Jefferson

The government should nationalize it! Socialized, single-payer video game development and sales now! More, cheaper, better games, right? Right?

Last edited by Beerina; 13th August 2017 at 02:32 AM.
Beerina is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 04:54 AM   #3
ceptimus
puzzler
 
Join Date: May 2003
Posts: 4,648
Originally Posted by psionl0 View Post
About the only advantage I can see of a 120V system is that local power lines can be thinner since they carry less current.
That's the wrong way round. For any given appliance of a certain power, the 120V unit will consume twice the current of its 240V equivalent - so a 120V system will usually require thicker wiring and power cords.

There are two causes of thick wiring and cords - one is to provide more conductor cross section to carry higher currents - the other is to have greater insulation thickness to protect against electric shock or shorts. Generally speaking there is a trade off in thickness as the voltage is raised - a higher voltage cable carries less current for the same power, so the conductor can be thinner, but the higher voltage cable also requires thicker insulation to be safe, so the insulation is thicker.

I think with correctly specified cables to "code" the 240V ones will usually be a bit thinner than 120V ones - especially for higher power appliances like kettles.

Last edited by ceptimus; 13th August 2017 at 04:55 AM.
ceptimus is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 05:14 AM   #4
PhantomWolf
Penultimate Amazing
 
PhantomWolf's Avatar
 
Join Date: Mar 2007
Posts: 15,714
Originally Posted by Beerina View Post
It's to stop you from insta-dying if you get shocked. Or at least reduce your chances.

US houses typically have 240 available for electric stoves, and general home equipment is 120.


My dad, rest his soul, as a child (this would be mid 1940s) fell in the tub, dropping a radio in with him. My grandmother had to run down into the basement and flip the main off.

I'll leave it to you as to whether the 120 volts killed my father when he was 6 or not.
Volts don't kill you at all.

Consider the Taser, it has a wallop of about 50,000 Volts.

What will kill you is the Amperage, about 100-200 mA across the heart.
__________________

It must be fun to lead a life completely unburdened by reality. -- JayUtah
I am not able to rightly apprehend the kind of confusion of ideas that could provoke such a question. -- Charles Babbage (1791-1871)
My Apollo Page.
PhantomWolf is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 05:54 AM   #5
surrogate
Critical Thinker
 
surrogate's Avatar
 
Join Date: Aug 2007
Location: Somewhere within the Orion Arm
Posts: 317
Originally Posted by psionl0 View Post

America, Canada, Japan and a few other countries use a 120V mains. There the setup seems a little more complicated. As I understand it, the local power lines carry 7,200V and pole top (or underground) transformers convert it to a "center tapped" 240V supply (http://science.howstuffworks.com/env...rgy/power7.htm). Each transformer supplies a single house with two phase 120V electricity (although residential complexes may share a transformer). Heavy duty appliances like washing machines can easily be accommodated with 240V but if a household needs a three phase supply then I guess they need an extra pole top transformer.
I think it is called split phase, not two phase. US Washing machines (non commercial) are 120V, electric hot water heaters, stoves, dryers, and central heating units are generally 240V.
surrogate is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 06:11 AM   #6
psionl0
Skeptical about skeptics
 
psionl0's Avatar
 
Join Date: Sep 2010
Location: 31°57'S 115°57'E
Posts: 11,221
Originally Posted by ceptimus View Post
That's the wrong way round. For any given appliance of a certain power, the 120V unit will consume twice the current of its 240V equivalent - so a 120V system will usually require thicker wiring and power cords.
You are conflating power lines with power cords.

In any case, you didn't read the link I provided. US power poles have 7,200 V at the lines while in the rest of the world it is 240 V.
__________________
"The process by which banks create money is so simple that the mind is repelled. Where something so important is involved, a deeper mystery seems only decent." - Galbraith, 1975
psionl0 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 06:11 AM   #7
Speedskater
Scholar
 
Join Date: Mar 2006
Posts: 120
In the US system, the same wires are used in the 120V and 240V parts of the system.

================
NEC Article 310

Last edited by Speedskater; 13th August 2017 at 06:18 AM. Reason: added content
Speedskater is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 06:13 AM   #8
Modified
Philosopher
 
Modified's Avatar
 
Join Date: Sep 2006
Posts: 6,337
Originally Posted by PhantomWolf View Post
Volts don't kill you at all.

Consider the Taser, it has a wallop of about 50,000 Volts.

What will kill you is the Amperage, about 100-200 mA across the heart.
And with double the voltage, all else being equal and where there is no current limitation, you will get twice the current. A Taser is current-limited.

Last edited by Modified; 13th August 2017 at 06:19 AM.
Modified is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 06:16 AM   #9
Modified
Philosopher
 
Modified's Avatar
 
Join Date: Sep 2006
Posts: 6,337
Originally Posted by Speedskater View Post
In the US system, the same wires are used in the 120V and 240V parts of the system.
They could be, but most houses I've lived in have dedicated lines for all the 240v equipment.
Modified is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 06:20 AM   #10
Speedskater
Scholar
 
Join Date: Mar 2006
Posts: 120
Yes, of course. But both the 120V and 240V circuits use the same type of wire. With the exact same insulation thickness. Probably from the same reels.

Last edited by Speedskater; 13th August 2017 at 06:21 AM.
Speedskater is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 06:56 AM   #11
aleCcowaN
imperfecto del subjuntivo
 
aleCcowaN's Avatar
 
Join Date: Jul 2009
Location: stranded at Buenos Aires, a city that, like NYC or Paris, has so little to offer...
Posts: 7,492
Regarding mains electricity, the most common voltage is 230 V -like Australia's- followed by 220 V and 120V, with several countries using 240V, 115V, 110V and 127V. The most common frequency is 50 Hz, with many countries using 60 Hz. I'm positive Edison's 110V wounds up being statistically safer than 230V when people do what they must avoid or neglect to check and keep their wiring.

Besides that:

There's a continent called America with no unified mains electricity voltage.

120/240 V household electricity is not "two phase" at all. It is one phase, two voltages and 4 wires (that is the "mess" mentioned) In a normal country you have 4 wires to enjoy polyphase and single-phase at the same time in a whole apartment building, and even you can have just 3 wires and have three-phase and single-phase at the same exact voltage with the electric service company just using 2 transformers and not 3 (that is typical in quick developing areas).

I have had at home 3 x 220V without ground, later 3 x 380/220V without ground and now 3x 380/220V with ground. There was a time when I had to warn any electrician coming to do some work at home that he needed to be careful because both wires were "hot". They were very "sceptic" about my knowledge but they kept silent once they had finished their works. One of them was shocked and felt for not using proper footwear while handling the "neutral", without having had the common-knowledge precaution of touching it first with the first knuckle of his index, just below the nail.

I remember that, 35 years ago, each time I had electricity but the lift wasn't working or did strange noises I'd took my first multimeter and check all three phases by measuring the voltage between hot an "neutral" wire, hot and the kitchen tap and "neutral" and the kitchen tap. Public company ages, long gone now.

PS: People who don't know what phase means in power provision shouldn't speak of it.

PS2: There was a kid who said to be shocked in a bathtub just to avoid to be punished by letting a radio drop into it. Maybe we're talking of the same kid.
__________________
Horrible dipsomaniacs and other addicts, be gone and get treated, or covfefe your soul!
These fora are full of scientists and specialists. Most of them turn back to pumpkins the second they log out.
I got tired of the actual schizophrenics that are taking hold part of the forum and decided to do something about it.
aleCcowaN is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 07:01 AM   #12
ceptimus
puzzler
 
Join Date: May 2003
Posts: 4,648
Originally Posted by psionl0 View Post
You are conflating power lines with power cords.

In any case, you didn't read the link I provided. US power poles have 7,200 V at the lines while in the rest of the world it is 240 V.
No. I'm right and you're wrong.

Power (Watts) is volts times amps. A 1.2 kW appliance, assuming near-unity power factor, will draw ten amps from a 120V supply, but only five amps from a 240V one. If the power factor is bad, it will draw even more amps - the power is actually volts x amps x cos(phi). However, most household appliances, especially the higher power ones, will have good power factors.

We have various transmission line voltages here from 400 kV, 135 kV, down to normal factory 3-phase which is 415V between phases (actually 440V but now called 415 to be Eu-compliant). Phase to neutral (or earth) is then 240V (but now called 230V). For houses the three-phase runs down the street (usually underground) and only a single phase, plus neutral and earth is bought into each house. Different houses along the street run on different phases in an attempt to balance the load across the three phases. This means that if you run an extension cord from your house, and your neighbour does the same, then you can potentially get an electric shock from phase-to-phase of 415V (or 440V) in the unlikely event that both extension leads or appliances plugged into them are faulty and you touch both appliances at the same time.

Everything in the UK is 50Hz which is slightly unusual as the majority of countries now operate at 60Hz, regardless of the voltage.

Last edited by ceptimus; 13th August 2017 at 07:20 AM.
ceptimus is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 07:05 AM   #13
ceptimus
puzzler
 
Join Date: May 2003
Posts: 4,648
When the UK changed from 240V to 230V (to be compliant with Europe), the voltage didn't change at all. They just started putting 230V stickers on things - there was already a sufficient tolerance that meant that our 240V supply was compliant with the new regulations and labels.
ceptimus is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 07:28 AM   #14
aleCcowaN
imperfecto del subjuntivo
 
aleCcowaN's Avatar
 
Join Date: Jul 2009
Location: stranded at Buenos Aires, a city that, like NYC or Paris, has so little to offer...
Posts: 7,492
Originally Posted by ceptimus View Post
We have various transmission line voltages here from 400 kV, 135 kV, down to normal factory 3-phase which is 415V between phases (actually 440V but now called 415 to be Eu-compliant).
It was 415V when it was 240V. For 230V it corresponds 400V. It's just basic trigonometry, so to speak: 230V x 2 x sin 60°. Of course they're allowed to provide up to 6% more than that, and in some countries even 10% just to force consumption when the overall load is low and technical minimals from nuclear power plants and fossil fuel plants are to be kept. I once measured 247V at home (normal is 223V) at 3:30 am (I was curious why the light seemed to be so bright).
__________________
Horrible dipsomaniacs and other addicts, be gone and get treated, or covfefe your soul!
These fora are full of scientists and specialists. Most of them turn back to pumpkins the second they log out.
I got tired of the actual schizophrenics that are taking hold part of the forum and decided to do something about it.
aleCcowaN is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 08:09 AM   #15
Macgyver1968
Philosopher
 
Macgyver1968's Avatar
 
Join Date: Jan 2009
Location: Dallas, Texas
Posts: 5,136
Originally Posted by PhantomWolf View Post
Volts don't kill you at all.

Consider the Taser, it has a wallop of about 50,000 Volts.

What will kill you is the Amperage, about 100-200 mA across the heart.
I never liked that phrase. To me, it's like saying "It's not the gunpowder that kills you, it's the lead projectile." When in fact, it's the right combination of both that kills you.
__________________
"Fixin' crap that ain't broke."
Macgyver1968 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 08:11 AM   #16
Modified
Philosopher
 
Modified's Avatar
 
Join Date: Sep 2006
Posts: 6,337
Originally Posted by aleCcowaN View Post
120/240 V household electricity is not "two phase" at all. It is one phase, two voltages and 4 wires (that is the "mess" mentioned)
It's two 120 volt lines relative to ground, 180 degrees out of phase. There is no 240 volt line.
Modified is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:01 AM   #17
aleCcowaN
imperfecto del subjuntivo
 
aleCcowaN's Avatar
 
Join Date: Jul 2009
Location: stranded at Buenos Aires, a city that, like NYC or Paris, has so little to offer...
Posts: 7,492
Originally Posted by Modified
Originally Posted by aleCcowaN View Post
120/240 V household electricity is not "two phase" at all. It is one phase, two voltages and 4 wires (that is the "mess" mentioned)
It's two 120 volt lines relative to ground, 180 degrees out of phase. There is no 240 volt line.
What doesn't contradict what I said. That "180 degrees out of phase" is what you see, not two phases. It's called a split-phase electric power. This figure in it



shows the only transformer for the only phase in it. An autotransformer isn't neither two-or-more phased.
__________________
Horrible dipsomaniacs and other addicts, be gone and get treated, or covfefe your soul!
These fora are full of scientists and specialists. Most of them turn back to pumpkins the second they log out.
I got tired of the actual schizophrenics that are taking hold part of the forum and decided to do something about it.
aleCcowaN is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:08 AM   #18
MostlyDead
Graduate Poster
 
MostlyDead's Avatar
 
Join Date: Aug 2016
Posts: 1,577
Originally Posted by Speedskater View Post
In the US system, the same wires are used in the 120V and 240V parts of the system.

================
NEC Article 310
Per NEC, it depends on the amperage. 14 or 12 gauge wiring is used for 120v, but the higher amp draw of 240v normally requires 10 or 8 gauge wiring, in the instance of the household appliances listed earlier.
__________________
Thusly blathered MostlyDead
MostlyDead is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:25 AM   #19
Dabop
Critical Thinker
 
Join Date: May 2015
Location: Oz
Posts: 302
Originally Posted by MostlyDead View Post
Per NEC, it depends on the amperage. 14 or 12 gauge wiring is used for 120v, but the higher amp draw of 240v normally requires 10 or 8 gauge wiring, in the instance of the household appliances listed earlier.
Um hate to be contrary, but this is 100% completely, totally and utterly wrong...
W=V x A (commonly known as watts law)
shows conclusively that doubling the voltage will HALVE the current for the same wattage drawn

thus for the same circuit loading (ie watts consumed by the load) the current will HALVE when using 240VAC compared to 120VAC

either that or I have been doing it wrong for the last 35 years.....along with every other electrician in the world

as an example, being the middle of winter, I have my 2400W fan heater going in the bedroom ATM
this draws 10A from my 240VAC (nominal) outlet (which is now classified as 230VAC, despite the normal voltage as read by my Fluke meter usually being 247V...)
If I was in the states, using their 110/120VAC system, to get the same 2400W heating, I would have to halve the resistance of the heating element, which would result in a 20A draw to get the same 2400W heating effect

Thus by halving the voltage I have doubled the current- as was foretold by Watts Law...
__________________
It's a kind of a strawman thing in that it's exactly a strawman thing. Loss Leader

Last edited by Dabop; 13th August 2017 at 09:33 AM. Reason: added example
Dabop is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:32 AM   #20
MostlyDead
Graduate Poster
 
MostlyDead's Avatar
 
Join Date: Aug 2016
Posts: 1,577
Originally Posted by Dabop View Post
Um hate to be contrary, but this is 100% completely, totally and utterly wrong...
W=V x A (commonly known as watts law)
shows conclusively that doubling the voltage will HALVE the current for the same wattage drawn

thus for the same circuit loading (ie watts consumed by the load) the current will HALVE when using 240VAC compared to 120VAC

either that or I have been doing it wrong for the last 35 years.....along with every other electrician in the world
Ok. So you are wiring up a 50 amp 220v circuit for, say, an electric oven with I would assume 14 gauge, and passing inspection per NEC? I hope you'll forgive me for not continuing this argument.

ETA: we were talking about wiring for 240v household appliances (stoves, water heaters, dryers, etc.). All obviously high wattage draw. While you are right on the watt calc, it was irrelevant to the subject of 240v household appliances. They are all high wattage, and in construction terms automatically high amperage.
__________________
Thusly blathered MostlyDead

Last edited by MostlyDead; 13th August 2017 at 09:43 AM.
MostlyDead is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:34 AM   #21
bobdroege7
Master Poster
 
bobdroege7's Avatar
 
Join Date: May 2004
Posts: 2,201
I know that it's made 3 phase 120 degrees apart, so if you have 240 two phase power, it's 120 degrees apart, not 180.
__________________
Un-american Jack-booted thug

Graduate of a liberal arts college!

Faster play faster faster play faster
bobdroege7 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:44 AM   #22
aleCcowaN
imperfecto del subjuntivo
 
aleCcowaN's Avatar
 
Join Date: Jul 2009
Location: stranded at Buenos Aires, a city that, like NYC or Paris, has so little to offer...
Posts: 7,492
Originally Posted by bobdroege7 View Post
I know that it's made 3 phase 120 degrees apart, so if you have 240 two phase power, it's 120 degrees apart, not 180.
You should understand what polyphase is in this context before reaching any conclusion.

A 240V two phase power 120 degrees apart is the three-phase system called in Spanish "triángulo abierta" that I mentioned above. When I translate it into "open delta" -which is the right translation of the concept in the name- it seems to refer to a different thing.
__________________
Horrible dipsomaniacs and other addicts, be gone and get treated, or covfefe your soul!
These fora are full of scientists and specialists. Most of them turn back to pumpkins the second they log out.
I got tired of the actual schizophrenics that are taking hold part of the forum and decided to do something about it.
aleCcowaN is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:46 AM   #23
Trebuchet
Penultimate Amazing
 
Trebuchet's Avatar
 
Join Date: Nov 2003
Location: The Great Northwet
Posts: 12,389
I think it's rare these days, but 208V three phase with a neutral provides a convenient 120V from each phase to the neutral. Very early in my engineering career I actually got to design a machine for that. We could eliminate the usual transformer to provide 120V for the control circuitry.
__________________
Cum catapultae proscribeantur tum soli proscripti catapultas habeant.
Trebuchet is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:46 AM   #24
DGM
Skeptic not Atheist
 
DGM's Avatar
 
Join Date: May 2007
Location: West of Northshore MA
Posts: 24,183
Originally Posted by MostlyDead View Post
Ok. So you are wiring up a 50 amp 220v circuit for, say, an electric oven with I would assume 14 gauge, and passing inspection per NEC? I hope you'll forgive me for not continuing this argument.

ETA: we were talking about wiring for 240v household appliances (stoves, water heaters, dryers, etc.). All obviously high wattage draw. While you are right on the watt calc, it was irrelevant to the subject of 240v household appliances. They are all high wattage, and in construction terms automatically high amperage.
That's not what he's saying. In my shop I have 10 amp and 20 amp 220v circuits that run with 14 and 12 gauge wire running small machines.

The amount of (expected) draw determines the wire size.
__________________
"Remember that the goal of conspiracy rhetoric is to bog down the discussion, not to make progress toward a solution" Jay Windley

"How many leaves on the seventh branch of the fourth tree?" is meaningless when you are in the wrong forest: ozeco41
DGM is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:46 AM   #25
Dabop
Critical Thinker
 
Join Date: May 2015
Location: Oz
Posts: 302
As we dont work with these 'gauge' wires, I would have to consult google to find out what size they actually are, but I can state with 100% accuracy, and I'll support with links, that if you want the same load (stated in watts) then it will 100% guaranteed halve the current every time you double the voltage

(what is the NEC- I assume from your comment it is some kind of regulatory body in the US???)- The only NEC I have come across here makes cash registers and the like, and altho the power companies certainly have no qualms about taking my cash, I doubt they have much to do with the wiring codes...)

;-)
__________________
It's a kind of a strawman thing in that it's exactly a strawman thing. Loss Leader
Dabop is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:50 AM   #26
MostlyDead
Graduate Poster
 
MostlyDead's Avatar
 
Join Date: Aug 2016
Posts: 1,577
Originally Posted by Dabop View Post
As we dont work with these 'gauge' wires, I would have to consult google to find out what size they actually are, but I can state with 100% accuracy, and I'll support with links, that if you want the same load (stated in watts) then it will 100% guaranteed halve the current every time you double the voltage

(what is the NEC- I assume from your comment it is some kind of regulatory body in the US???)- The only NEC I have come across here makes cash registers and the like, and altho the power companies certainly have no qualms about taking my cash, I doubt they have much to do with the wiring codes...)

;-)
National Electrcal Code, part of National Fire Prevention code
__________________
Thusly blathered MostlyDead
MostlyDead is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:51 AM   #27
DGM
Skeptic not Atheist
 
DGM's Avatar
 
Join Date: May 2007
Location: West of Northshore MA
Posts: 24,183
Originally Posted by Dabop View Post
(what is the NEC- I assume from your comment it is some kind of regulatory body in the US???)- The only NEC I have come across here makes cash registers and the like, and altho the power companies certainly have no qualms about taking my cash, I doubt they have much to do with the wiring codes...)

;-)
National Electric Code. It's a huge catalog of information put into the most complicated way possible.............
__________________
"Remember that the goal of conspiracy rhetoric is to bog down the discussion, not to make progress toward a solution" Jay Windley

"How many leaves on the seventh branch of the fourth tree?" is meaningless when you are in the wrong forest: ozeco41
DGM is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:54 AM   #28
Dr.Sid
Graduate Poster
 
Join Date: Sep 2009
Location: Olomouc, Czech Republic
Posts: 1,181
Originally Posted by Macgyver1968 View Post
I never liked that phrase. To me, it's like saying "It's not the gunpowder that kills you, it's the lead projectile." When in fact, it's the right combination of both that kills you.
It's different .. voltage and current are 2 sides of the same coin (well, together with resistance) you can't have one without another. Gunpowder and bullet are just two things.

120V is safer for sure, but it's by no means 100% safe.
Dr.Sid is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:57 AM   #29
Dabop
Critical Thinker
 
Join Date: May 2015
Location: Oz
Posts: 302
12 0.0808 2.05
13 0.0720 1.83
14 0.0641 1.63
15 0.0571 1.45


OK weird yank wire sizes figured out in real measurements ie mm^2
I have heard of these 'gauge' wires but never had to deal with imperial units, even when we had feet and inches we still used fractions of an inch ^2 for cable sizes

The only 12 gauge I have ever used went boom and was good on rabbits....
__________________
It's a kind of a strawman thing in that it's exactly a strawman thing. Loss Leader
Dabop is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 09:59 AM   #30
MostlyDead
Graduate Poster
 
MostlyDead's Avatar
 
Join Date: Aug 2016
Posts: 1,577
Originally Posted by DGM View Post
That's not what he's saying. In my shop I have 10 amp and 20 amp 220v circuits that run with 14 and 12 gauge wire running small machines.

The amount of (expected) draw determines the wire size.
Yes, that's what I said. Talking about ovens and water heaters in household 220v, it's all high expected draw. Becomes a pedantic argument to say there is a lighter gauge for household appliance wiring when it basically does not exist.
__________________
Thusly blathered MostlyDead
MostlyDead is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:01 AM   #31
Dabop
Critical Thinker
 
Join Date: May 2015
Location: Oz
Posts: 302
Originally Posted by DGM View Post
National Electric Code. It's a huge catalog of information put into the most complicated way possible.............
Ahhh....


we have our own version of that
less sexy title tho

AS/NZS 3000:2007

doesnt roll off the tongue quite like NEC tho does it
__________________
It's a kind of a strawman thing in that it's exactly a strawman thing. Loss Leader
Dabop is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:07 AM   #32
Dabop
Critical Thinker
 
Join Date: May 2015
Location: Oz
Posts: 302
Originally Posted by MostlyDead View Post
Yes, that's what I said. Talking about ovens and water heaters in household 220v, it's all high expected draw. Becomes a pedantic argument to say there is a lighter gauge for household appliance wiring when it basically does not exist.
Actually here it does
but thats not what you said, "14 or 12 gauge wiring is used for 120v, but the higher amp draw of 240v"

is a factually incorrect statement
240v doesnt 'draw' more amps, in your country it is used for higher wattage appliances, here it isnt- everything from my led desklamp to the 3600w hot water service is 240v

And to do the same amount of 'work' ie wattage consumed- the voltage when doubled, will halve the current- which is why we use 240vac in the first place
__________________
It's a kind of a strawman thing in that it's exactly a strawman thing. Loss Leader
Dabop is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:12 AM   #33
DGM
Skeptic not Atheist
 
DGM's Avatar
 
Join Date: May 2007
Location: West of Northshore MA
Posts: 24,183
Originally Posted by MostlyDead View Post
Yes, that's what I said. Talking about ovens and water heaters in household 220v, it's all high expected draw. Becomes a pedantic argument to say there is a lighter gauge for household appliance wiring when it basically does not exist.
These are not the only examples of 220v appliances used in the US.

Electric baseboard heat and A/C units along with bathroom heaters are good examples that are typically rated as 20 amp or less.

Your blanket statement is incorrect.
__________________
"Remember that the goal of conspiracy rhetoric is to bog down the discussion, not to make progress toward a solution" Jay Windley

"How many leaves on the seventh branch of the fourth tree?" is meaningless when you are in the wrong forest: ozeco41
DGM is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:12 AM   #34
aleCcowaN
imperfecto del subjuntivo
 
aleCcowaN's Avatar
 
Join Date: Jul 2009
Location: stranded at Buenos Aires, a city that, like NYC or Paris, has so little to offer...
Posts: 7,492
Originally Posted by Trebuchet View Post
I think it's rare these days, but 208V three phase with a neutral provides a convenient 120V from each phase to the neutral. Very early in my engineering career I actually got to design a machine for that. We could eliminate the usual transformer to provide 120V for the control circuitry.
Exactly: delta 208V is wye 208/sqrt(3)= 120V

but you never had needed a transformer: that's the way it's designed to be. You decided to plug it in one configuration and not the in the other.
__________________
Horrible dipsomaniacs and other addicts, be gone and get treated, or covfefe your soul!
These fora are full of scientists and specialists. Most of them turn back to pumpkins the second they log out.
I got tired of the actual schizophrenics that are taking hold part of the forum and decided to do something about it.
aleCcowaN is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:18 AM   #35
psionl0
Skeptical about skeptics
 
psionl0's Avatar
 
Join Date: Sep 2010
Location: 31°57'S 115°57'E
Posts: 11,221
Originally Posted by aleCcowaN View Post
PS: People who don't know what phase means in power provision shouldn't speak of it.
3 live to neutral voltages each 120 degrees out of phase relative to each other is 3 phase power.

But 2 live to neutral voltages both 180 degrees out of phase relative to each other is NOT 2 phase power. Got it.
__________________
"The process by which banks create money is so simple that the mind is repelled. Where something so important is involved, a deeper mystery seems only decent." - Galbraith, 1975
psionl0 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:21 AM   #36
psionl0
Skeptical about skeptics
 
psionl0's Avatar
 
Join Date: Sep 2010
Location: 31°57'S 115°57'E
Posts: 11,221
Originally Posted by ceptimus View Post
No. I'm right and you're wrong.
You are right if you are talking about something completely different to what I am posting.

I am referring to the power lines that run past your house and which you connect to in order to supply your house. (The 7,200 volt reference should have been a clue).
__________________
"The process by which banks create money is so simple that the mind is repelled. Where something so important is involved, a deeper mystery seems only decent." - Galbraith, 1975
psionl0 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:22 AM   #37
MostlyDead
Graduate Poster
 
MostlyDead's Avatar
 
Join Date: Aug 2016
Posts: 1,577
Originally Posted by Dabop View Post
Actually here it does
but thats not what you said, "14 or 12 gauge wiring is used for 120v, but the higher amp draw of 240v"

is a factually incorrect statement
240v doesnt 'draw' more amps, in your country it is used for higher wattage appliances, here it isnt- everything from my led desklamp to the 3600w hot water service is 240v

And to do the same amount of 'work' ie wattage consumed- the voltage when doubled, will halve the current- which is why we use 240vac in the first place
Yes, I get that Oz is wired differently than the States, and I of course agree with the wattage calcs. Context. This is the post I responded to:

Originally Posted by Speedskater View Post
In the US system, the same wires are used in the 120V and 240V parts of the system.

================
NEC Article 310
To use your phrasing, this is factually incorrect statement. The 220 supply lines in the States for the high draw appliances listed earlier are not the same gauge as the 110 lines.

ETA: calling it amp draw instead of wattage draw is just construction shorthand around these parts.
__________________
Thusly blathered MostlyDead

Last edited by MostlyDead; 13th August 2017 at 10:24 AM.
MostlyDead is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:26 AM   #38
aleCcowaN
imperfecto del subjuntivo
 
aleCcowaN's Avatar
 
Join Date: Jul 2009
Location: stranded at Buenos Aires, a city that, like NYC or Paris, has so little to offer...
Posts: 7,492
I add myself to the list of people boggled by that "gauge" thingy of those ethnic standards.

I declined to look for wire section. The "ampacity" of a "14 gauge" (my goodness!) is 15 Ampere in copper, so it must be between 2 and 2.5 square millimetres, if the same rules for wire life and safety are applied. If it's less than that, OMG! such wires in cardboard and match houses!

About some two-person debate: undoubtedly using 240V for the same energy consumption requires half of the current needed under 120V, but that won't make regulations any lighter regarding minimum wire section (or maximum "gauge" if you like that).
__________________
Horrible dipsomaniacs and other addicts, be gone and get treated, or covfefe your soul!
These fora are full of scientists and specialists. Most of them turn back to pumpkins the second they log out.
I got tired of the actual schizophrenics that are taking hold part of the forum and decided to do something about it.
aleCcowaN is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:26 AM   #39
DGM
Skeptic not Atheist
 
DGM's Avatar
 
Join Date: May 2007
Location: West of Northshore MA
Posts: 24,183
Originally Posted by Dabop View Post
Ahhh....


we have our own version of that
less sexy title tho

AS/NZS 3000:2007

doesnt roll off the tongue quite like NEC tho does it
It's really called: NFPA 70: National Electrical Code (NEC) (2017).



It changes constantly and is not cheap to keep up with.

http://www.nfpa.org/nec
__________________
"Remember that the goal of conspiracy rhetoric is to bog down the discussion, not to make progress toward a solution" Jay Windley

"How many leaves on the seventh branch of the fourth tree?" is meaningless when you are in the wrong forest: ozeco41

Last edited by DGM; 13th August 2017 at 10:28 AM.
DGM is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 13th August 2017, 10:32 AM   #40
Dabop
Critical Thinker
 
Join Date: May 2015
Location: Oz
Posts: 302
Originally Posted by psionl0 View Post
3 live to neutral voltages each 120 degrees out of phase relative to each other is 3 phase power.

But 2 live to neutral voltages both 180 degrees out of phase relative to each other is NOT 2 phase power. Got it.
Shrugs- well I agree with you psion10, it was referred to as 2 phase power here when it was still used (mostly in country areas in some states)

2 phases 180 deg apart was 2 phase, 3 phases 120 deg apart is 415v/440v 3 phase, uncommon to have a dedicated motor etc using 2 of 3 phases of 240v, but common to split loads over 2 phases in large households where the current drawn was going to exceed the street line supply of 70A (older) or 100A(newer) where you could have 2 of 3 phases connected to the house to provide sufficient power (solid neutral required in the install tho)

(solid neutral is where the neutral is capable of carrying the combined total of all three phases, light or floating neutral has the same sized conductor as any single active or line conductor and a solid neural has the neutral wire is much larger than any single active conductor)
__________________
It's a kind of a strawman thing in that it's exactly a strawman thing. Loss Leader
Dabop is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Reply

International Skeptics Forum » General Topics » Science, Mathematics, Medicine, and Technology

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -7. The time now is 08:00 PM.
Powered by vBulletin. Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
© 2014, TribeTech AB. All Rights Reserved.
This forum began as part of the James Randi Education Foundation (JREF). However, the forum now exists as
an independent entity with no affiliation with or endorsement by the JREF, including the section in reference to "JREF" topics.

Disclaimer: Messages posted in the Forum are solely the opinion of their authors.